Is it safe to use this power outlet with an induction cooktop? I’ve connected a single-burner induction cooktop to it, and now I’m wondering…
Good question. The picture you share here says 16A. What is the amperage draw on your induction cooktop? If it’s over 12A I probably would not use it. But I don’t know your local codes.
I know the maximum power is 3500W, but I tested it, and at the maximum setting it puts out a little over 2900W, according to the power outlet.
In the US, we don’t normally go over 80% of max current for continuous loads. If your max is 3500, then 3500/240=14.583 but if it’s 2900 then it’s 2900/240=12.0833. 80% of 16 is 12.8 so I guess I’d feel comfortable with the 2900W but not the 3500W.
Of course if the socket gets warm during use, I would worry.
Got it, in that case, I’ll use it for the fan instead, just to be on the safe side ![]()
Keep in mind that I’m just one guy trying to help. I am not familiar with your local electrical codes. Best of luck!
It is not as much as whether it can handle the amperage as I guess it probably can. I have used one with an 3.5kW electric radiator but it does not draw full power but builds up to. I have also used one with a PSU designed to put out a smooth 13v DC. On switch on that can be quite a draw of power as the PSU needs to “fill” its capacitors in order to ensure a smooth, stable 13 volt output. My PSU is rated at up to 25 amps. I have had no problems but would advise care. Use an automation to ensure the plug is switched off by a given time in case you forget. I do that with all my smart plugs where phone charges and the like may be connected despite they being a low current drain. I have a PSU I don’t use anymore and in the early version of the Philips Smart Plug it worked for a few weeks and then “blew” the smart plug. Left it in an on position. The initial draw of current will have welded the relays inside the plug. That was though when they were beta testing them. If using a high amperage device take care.
Yup, just like @rhlangdon said, appliances with motors or large capacitors (or coils) have an inrush current that may even cause the breaker to trip, but they may be really “tamed down” during normal operations. This means that some devices like refrigerators, AC, induction stoves, more powerful power supplies may draw up to 15-30A for a split second.
This may be even much above the breaker max amperage, but breakers behave a bit differently in some situations (and the power spike may be too quick to trip them).
So this inrush current is ok for the whole electrical installation, but it may fry some electronics if they’re not meant to be used with such appliances.
But I can confirm that Aqara Wall Outlet H2 works ok with fridges, ovens and microwave ovens, so it should also be suitable for the induction stovetop. I cannot say for sure if Smart Plug H2 will be ok.