I would like to use an Aqara Dual Relay Module T2 (DCM-K01) to control only the Comfort and Eco modes of an electric Thermor Mozart Digital radiator equipped with a 230 V pilot wire.
When no command is sent through the pilot wire, the radiator operates in Comfort mode. I would therefore like to use a relay to send the Eco command.
Could you please confirm whether the T2 can be used for this purpose? If so, which contact mode should be selected (dry contact or powered contact), which terminals should be used, and whether any additional components are required?
I would like to keep the radiator’s normal mains power supply permanently connected and use the module exclusively to control the pilot wire.
@Jtou1 Hey there! Great question — using the T2 with a pilot wire radiator is a really interesting use case.
From what I can see in the reference docs, the Dual Relay Module T2 supports both dry contact and wet contact modes, which gives you flexibility for different setups. However, the specific scenario of a 230 V pilot wire for a Thermor radiator isn’t explicitly covered in the available materials.
Here’s what I can tell you based on the general wiring principles:
For your pilot wire application, you’ll likely want to consider:
Dry contact mode — this is typically used when you’re switching a control signal rather than mains power directly. The docs mention this mode is suitable for “thermostat” type applications like boiler control, which conceptually aligns with your radiator’s pilot wire control.
Wiring: In dry contact mode, you’d remove the jumper between LIN and LOUT, then use L1 or L2 for your switched pilot wire output, with LOUT as your common return.
Important: The T2 still needs its own L (live) and N (neutral) for power.
However, since your pilot wire operates at 230 V and the specific signaling protocol (resistive load, voltage presence/absence, or pulse patterns) for the Thermor Mozart Digital isn’t documented in our references, I’d strongly recommend verifying compatibility before wiring.
For a definitive answer on whether the T2’s relay characteristics match your radiator’s pilot wire requirements — and to avoid any risk of damaging either device — I’d suggest reaching out directly:
Contact the Aqara Home App Customer Service Team (Profile> Help & Feedback > Customer Service) or scan the QR code:
This will be more efficient. If you do not have an Aqara Home account, please click here to create a ticket.
If you do test this setup, it’d be awesome if you could share your results back here — pilot wire integrations aren’t commonly discussed, and your experience would definitely help others in the community
Good news: yes, the T2 can do this, and it’s actually the easiest pilot-wire case.
On a standard French 6-order pilot wire, Comfort = no signal and Eco = full 230 V sine wave (live) on the pilot wire. So switching between Comfort and Eco just means putting the live on the pilot wire, or taking it off. No diode needed.
Simplest wiring (wet contact mode):
Keep the red jumper between LIN and LOUT
L and N go to the same circuit and breaker that feeds the radiator
L1 goes to the radiator’s pilot wire (usually black)
Leave the radiator’s own L/N permanently connected, exactly as you planned
Relay ON = Eco, relay OFF = Comfort
Dry contact mode also works if you feed the radiator’s live into LOUT, but wet mode gets you the same result with fewer wires. The pilot-wire current is tiny, so load isn’t a concern.
Things to watch out for:
Feed the T2 from the same breaker/phase as the radiator. That way the signal is referenced to the right neutral, and switching off the breaker really kills everything in the box.
Never connect the pilot wire to neutral or earth.
On the radiator, check that it’s in its pilot-wire/programming mode (not manual), or it will happily ignore your Eco orders like a teenager.
Bonus: the second channel (L2), combined with a diode, could later add Frost-protection (negative half-wave) or Off (positive half-wave). Just don’t turn both channels on at the same time.
As always with 230 V: power off at the breaker before wiring, and if in doubt, get an electrician.
I’d now like to extend the setup to control four pilot-wire states from the Aqara app: Comfort, Eco, Frost Protection (Hors Gel), and Off (heating stopped).
My radiator is a Thermor Mozart Digital, 1,000 W, with a standard French 6-order pilot wire. I have an Aqara Dual Relay Module T2 (DCM-K01) and am considering using two 1N4007 diodes, connected in opposite directions, to generate the positive and negative half-wave signals.
Could you please confirm whether this wiring principle is correct?
Keep the red jumper between LIN and LOUT (wet-contact mode).
Power the T2 from the same circuit and breaker as the radiator, with the radiator’s own L and N remaining permanently connected.
Connect the T2’s L1 and L2 relay outputs to the pilot wire through two 1N4007 diodes, oriented in opposite directions, with both branches joining at the radiator’s pilot-wire input.
A few practical questions:
Relay states and diode orientation: Which combination of L1/L2 ON/OFF produces Comfort, Eco, Frost Protection, and Off? For each diode, should the cathode (the end marked with the band) face the T2 output or the radiator’s pilot wire? Is it safe to turn both relays ON simultaneously?
Connections: Is a WAGO connector suitable for joining the two diode branches and the pilot wire? How should the diode leads and joints be insulated and enclosed for a permanent 230 V installation?
Diode suitability: Is the 1N4007 (1 A, 1,000 V maximum repetitive reverse voltage) suitable for this application, or would you recommend another diode or circuit?
Radiator compatibility and testing: Is there anything specific about the Thermor Mozart Digital that could prevent it from correctly interpreting these half-wave signals? What tests would you recommend before deploying the same setup on three radiators?
I understand that this is a mains-voltage installation and that a qualified electrician will carry out the wiring. I’d like to have the circuit and relay-state mapping validated before installation.