Hello Aqara Support,
I am reporting a firmware issue with the Aqara Radiator Thermostat W600 (WT-A03E).
Device details:
Model: W600 (WT-A03E), Zigbee
Firmware: 0.0.0_2848 (stack 7216)
External room sensor: Aqara W100
Controller: Home Assistant with Zigbee2MQTT 2.14.1
Problem: When the temperature source is set to “external”, the W600 accepts and displays the external temperature, but the valve control still appears to follow the internal sensor.
Test performed:
Setpoint: 25 °C
Temperature source: external
External temperature: 28 °C, re-sent every 2 minutes for 40 minutes
Internal sensor: approximately 21 °C
Expected:
The valve should close because the external room temperature is 3 °C above the setpoint.
Actual result:
The valve continued opening, increasing from approximately 35% → 53% → 74%, with changes roughly every 15 minutes, apparently following the internal sensor.
The temperature source remained set to “external” throughout the entire test.
For comparison, my Aqara E1 thermostats in the same setup react correctly to the external temperature.
Workaround:
I can set the W600 to use the internal sensor and apply a temperature calibration/offset from Home Assistant so that it matches the W100. However, the calibration is limited to ±5 °C and 0.5 °C steps, which may not be sufficient in all situations, especially when the radiator is hot.
Other users appear to report similar behaviour, including when using an Aqara Hub and the Aqara Home app:
https://github.com/Koenkk/zigbee-herdsman-converters/issues/10812�
I currently have three W600 thermostats and planned to replace my Aqara E1 thermostats with the W600 while using Aqara W100 sensors for room temperature control.
Since the W600 is advertised as supporting an external sensor such as the W100, this appears to be a firmware issue.
Could you please tell me:
Is a firmware fix for external-sensor valve control planned?
If so, is there an estimated timeframe?
Is a beta firmware with this fix available for testing?
I would be happy to test beta firmware and provide logs or additional test results if needed.
Hi there, it looks like you’re experiencing a support-related issue. We’ve automatically created a support ticket for you and will reach out via the forum email within the next two business days.
If other members have any suggestions or insights on this topic, feel free to share!
Please pay attention to this issue.
@Aqarateam @AqaraOfficial
I have exactly the same issue and reproduced this. It’s completely unworkable with either the W100 or the T1 temperature sensor connected as external sensor. I want the room temperature to lead the valve position when the external sensor is coupled. With a wall temperature of 18 degrees the valve stays open until it reaches the setpoint compared to the internal sensor, instead of the room temperature reported by either the W100 or the T1. It’s completely unworkable and creates a higher energy bill then without.
Please @AqaraOfficial get this sorted out, currently I’m contempleting returning 24 W600’s as this solution does not work as advertised.
Thanks.
Hi all, I was about to buy several W600s (Zigbee mode, with Hub M3), but this thread honestly made me hesitate. It has been almost a month since the original report and there is still no response from Aqara staff, only the automated bot message.
Could the Aqara team please confirm whether this is a known firmware bug in 0.0.0_2848, and whether a fix is planned? Even a rough timeline would help those of us deciding whether to buy now or wait.
Thanks.
Hi there, we’re looking into this.
Hi @Caroline_Zzz,
Please DM me on the matter. I’m eager and willing to test a beta firmware on this, but we must act swiftly as I will be returning them within a week to be able to get my money back. I have an extensive setup and can test both the hub connect route or an extensive route in HA.
Please make this a quick one, it feels like it’s just a reference issue in the FW.
Thanks
Hello,
I have the same issue with the W600 and W100.
Link to the update:
Could not reproduce the external-sensor bug on W600 FW48 — detailed 2.8 h measurement, 4 rooms
I read this thread before the heating season started and wanted to check my own
setup properly, because I run four W600 with external sensors. Short version:
I could not reproduce the fault. Below is what I did, what I measured, and
where my test is weaker than I would like — so you can judge it yourself and
maybe spot what is different between our installations.
Setup
Four W600 (firmware 48) on an Aqara Hub M3 via Zigbee, M3 bridged into Home
Assistant 2026.10.4 over Matter.
| Room | External sensor | Sensor type |
|---|---|---|
| Playroom | Klima Puppenzimmer | Climate Sensor W100 |
| Dining room | Klima Esszimmer | Temp/Humidity Sensor |
| Child’s room | Klima Linus | Temp/Humidity Sensor |
| Basement room | Klima Partykeller | Temp/Humidity Sensor |
In all four rooms the W600 display tracks the external sensor to within
0.01–0.04 K. That part clearly works.
The measurement problem
The Matter bridge of the M3 exposes no valve position, no pi_heating_demand
and no hvac_action — only target temperature, current temperature, battery
(supported_features: 385). I also checked whether HA creates such entities
hidden or disabled (it does not), and whether the Matter attribute
PIHeatingDemand can be read directly (matter/read_attribute does not exist
in HA, and the Matter server add-on is not reachable from outside).
So unlike the user who posted valve percentages, I had to use substitutes:
- Radiator surface temperature with an IR thermometer, top and bottom.
All values are maxima — I traced along the radiator and took the hottest
spot, consistently in every round. - Touching the supply pipe just before the valve.
- Room temperature curve from the external sensor, logged every minute via
the HA REST API (159 data points).
Important: which test actually separates the hypotheses
This tripped me up at first, so it is worth stating.
Test B (setpoint below external sensor, “room too warm”) does not
separate them. With the valve closed, the thermostat head settles near room
temperature — which by definition is above the setpoint here. So an
internally-regulating valve would also stay shut. Test B only checks whether
the symptom from this thread occurs, i.e. a valve opening spontaneously.
Test A (setpoint above external sensor) separates them only in rooms whose
temperature does not rise much: the radiator gets hot, the internal sensor
goes above setpoint, but the external deviation stays large. Internal regulation
→ valve closes. External regulation → valve stays open. In rooms that warm up
quickly, both variants throttle and the test tells you nothing.
That left me with two conclusive rooms.
The conclusive result (Test A, 09:02–10:19)
| Basement room | Dining room | |
|---|---|---|
| external sensor below setpoint | 1.56–1.99 K, all 84 samples | 1.04–1.55 K, all 84 samples |
| radiator surface 09:49 | 40.0 °C | 42.0 °C |
| radiator surface 10:06 | 40.5 °C | 44.3 °C |
| radiator surface 10:21 | 41.1 °C | 45.6 °C |
Both rooms stayed 1–2 K below setpoint for over an hour while the radiator sat
at 40–46 °C. A radiator at that temperature inevitably heats the thermostat head
far above a 20 °C setpoint. An internally-regulating valve would have had to
close. Neither did — the dining room valve actually kept opening further.
Additionally, in all four rooms the throttling tracked the size of the
external deviation: the basement at 2.0 K below setpoint stayed wide open,
while the child’s room at 0.46 K throttled hardest.
Test B (10:29–11:50)
Setpoint set 1.5–2.2 K below the external sensor in all four rooms.
| Room | surface 10:21 → 11:02 → 11:50 |
|---|---|
| Dining room | 45.6 → 30.6 → 24.4 °C |
| Basement room | 41.1 → 27.1 → 22.8 °C |
| Playroom | 38.2 → 26.0 → 23.0 °C |
| Child’s room | 28.1 → 22.4 → 23.0 °C |
All rooms stayed above setpoint for the full 75 minutes (74 samples each). All
radiators cooled monotonically, and at 11:50 all four supply pipes were cold
to the touch and getting colder, with the boiler supplying 43 °C flow
temperature. No valve opened. The case @zysk_kamil described (room 22 °C,
setpoint 18 °C, radiator fires up) did not occur here.
Where my test is weak — please read this before quoting me
- No actual valve position was measured. Everything about valve state is
inferred from surface temperature and touch. - The internal sensor value is not readable, so “internal sensor was above
setpoint” is inferred from a 40 °C radiator, not measured. - The W100 group has no conclusive result. Only one of my rooms uses a W100,
and that room happened to be one of the non-separating ones. I saw no
difference between sensor types, but for the W100 that statement rests on
nothing stronger than “symptom absent”. - My setpoint offset was 1.5–2.2 K, whereas the reported case used 4 K. I
did not run a harsher pass. - My firmware reads 48, not 0.0.0_2848 as reported here. I cannot tell from
my side whether that is the same build in a different notation.
So what is different between us?
Since the fault is clearly real for several of you, the interesting question is
what my setup does differently. Candidates I can see:
- Hub model — mine is an M3. What are you using?
- Firmware — if yours really is a different build, that would be the
simplest explanation. - How the external sensor is bound — mine are bound in the Aqara app,
sensor and thermostat in the same room, same hub. One report in this thread
used Zigbee2MQTT to inject the value, which is a different path entirely. - Firmware of the external sensor itself.
If anyone wants the raw data (per-minute CSV, IR readings, hand notes), say so
and I will post it. Happy to run a harsher pass with a 4 K offset if that helps
narrow it down.
The big problem here is as follows:
Push a setpoint at 19.5 degrees while temperature is 18 degrees: Valve opens propely and starts heating demand.
Have an actual setpoint of 19.5 degrees, but then the room temperature gradually goes down, let’s say in 30 mins to 19, then the next 30 mins to 18.5, then next 30 mins to 18 degrees.
This is exactly where the external temperature change does not invoke a valve position change, or a formal heat request.
It’s a very simply reference: if at any point there is a temperature shift (either changed setpoint, or changed room temperature - internal or externally measured) is where it fails.
If you want to test your setup try and invoke exactly that. Take the W100 off of the wall and place it in a cooler area and see / listen to what the valve does, and if it actually starts heating.
This is such a simple miss on the FW it sounds like this should never exist - but in my case, with multiple W600’s - it does.
There needs to be a constant review of current temperature (internal sensor or external) compared to setpoint and the valve position needs to alter based on the temperature delta.
@Caroline_Zzz please please have the team focus on having this work as intended. Thanks
I’m experiencing exactly the same issue with my Aqara W600 thermostats and external FP300 temperature sensors.
My radiators are enclosed, so reliable temperature control based on external sensors is essential for my setup . This is precisely why I purchased several W600 thermostats and FP300 sensors. Before purchasing, I explicitly contacted Aqara Support and received confirmation that this combination was compatible and would support native external temperature control.
I have tested multiple W600 thermostats with different FP300 sensors, pairing them in different combinations through Aqara Home. The result is always the same: The W600 correctly displays the external temperature measured by the FP300, but the valve still appears to regulate based on the W600’s internal temperature.
With the cold season starting, this issue is becoming increasingly urgent . My heating setup depends on this functionality, and the devices currently don’t work as advertised or as confirmed by Aqara Support.
Could someone from Aqara please provide an update on the investigation, confirm whether this is a known firmware issue, and share an estimated timeline for a fix?
Given that this affects a core advertised feature, I really hope Aqara will prioritize resolving it.
I have the same… Hub M3 and The Aqara W600 thermostat fails to stop heating in active (ON) mode. When set to 20.0°C, it keeps the radiator valve open even W100 is showing 22.5C, allowing water to flow. When I turn it off it close the valve.
I had high hopes for this device. Please, @AqaraTeam, fix this. Since the heating season is starting, if this issue isn’t resolved, I’ll need to reinstall my old thermostat radiators and return these under warranty.
I’ve encountered another issue with the radiator in my bathroom: I had the temperature set to 18°C, yet the radiator turned on when the room reached 22.5°C. I’ve had to turn off all the radiators to prevent them from switching on unexpectedly, and I’m now considering returning the unit—the fact that it heats up on its own is concerning, especially regarding the lack of control over heating during longer periods away from home.
Same problem here (firmware 0.0.0_2848) — please fix this
I have the same issue with 3 × W600 on firmware 0.0.0_2848.
While the valve was linked to an external temperature sensor, it looked as if it kept heating even though the target had already been exceeded: the valve showed the external sensor’s temperature (25.0 °C), the setpoint was 23 °C, and the valve position stayed at about 17 %. I couldn’t understand why, because with the sensor linked I could not see the valve’s internal temperature at all.
When I removed the link, the valve started reporting its internal probe: 22.5 °C, i.e. below the setpoint (and about 1.7 °C below the real room temperature: a separate thermometer next to the room sensor settled at 24.2 °C — the radiator is on an exterior wall). With that value the 17–18 % opening suddenly made sense. Only then did I understand the problem: the valve displays the external sensor, but it still regulates on its internal sensor. Another valve of mine closed only once its internal reading went above the setpoint.
| Valve | Linked? | Temp shown | Setpoint | Valve position |
|---|---|---|---|---|
| Living room | yes | 25.0 °C (external) | 23 °C | 17 % |
| Living room | no | 22.5 °C (internal) | 23 °C | 17–18 % |
| Kid’s room | yes | 24.3 °C (external) | 23 °C | 17–18 % |
| Kid’s room | no | 24.5 °C (internal) | 23 °C | 0 % |
Why this matters: radiators are almost always mounted on the exterior wall, and that wall is colder than the room. A sensor inside the valve body, right next to the radiator and the cold wall, simply cannot reflect the temperature inside the room. That is exactly why an external sensor is recommended in the first place. But a linked external sensor must not be just a value shown in the app — it has to be part of the valve’s control logic and actually drive the valve opening. Right now it is only displayed.
My own rooms confirm the wall effect: in the kid’s room the wall behind the radiator does not face the outside directly — there is an enclosed glass balcony (an unheated buffer room) beyond it. There the valve’s internal reading is close to the real room temperature (24.5 °C vs. 24.3 °C). In the living room, where the radiator sits on a wall facing the outside (about 9 °C outdoors), the internal probe reads about 1.7 °C low. So the internal probe is only “right” when the wall behind the radiator happens to be warm — which is not the typical installation.
I would also like to ask Aqara clearly to fix this: when an external sensor is linked, the valve should regulate on that sensor, not on its internal probe. Please let us know when a firmware fix for 2848 is planned.
Follow-up: the valve position cannot be set directly — only the setpoint moves the motor
I tested writing the valve position directly through the Aqara Cloud API (HeaterCooler.TRVValvePosition, which the API lists as writable):
- I wrote 50 %. The request was accepted and within 3 seconds the valve reported 50 %. But the radiator did not get warm at all and there was no motor sound.
- A few minutes later I wrote the setpoint
HeatingTemperature = 30 °Cinstead. The motor started immediately (audible), the valve reported 100 % and the radiator got hot right away.
So writing the position only changes the reported value; it does not move the valve. The only thing that really drives the valve is the setpoint: the W600 compares the setpoint with its internal sensor and decides the opening itself. Earlier I measured this on another valve (room and valve both at 25.2 °C): setpoint 26 → 27 %, 27 → 35 %, 28 → 43 %, i.e. the opening grows with the difference to the internal reading.
In practice this leaves only two reliable states: setpoint 30 °C = fully open, setpoint well below the internal reading (e.g. 15 °C) = fully closed. Everything in between depends on the internal probe — which, as I described above, reads too low because the radiator is on a cold exterior wall.
Request to Aqara: please add a real “set valve opening %” command — in the app, in automations and in the Cloud API (TRVValvePosition should actually move the valve, not only change the reported value). Together with the external-sensor fix this would let users and integrations drive the W600 based on the actual room temperature. Also, if a value is not meant to be writable, the API should reject the write instead of reporting it as if it had been applied.
I’ll second that statement regarding your request with an addition: The Valve position must also be writeable through Zigbee, and act accordingly.
Also, when you set the valve position - all other functions must cease to function. I don’t need to know the reported temperature by the TRV when I have control over the full hysteresis outside of the TRV. I don’t need to portray the current temperature when that’s visible on the W100 used to control how many % the valve is open.
Please fix this.
Update: Same issue with W100 and T1
I wanted to share an important update on my W600 external temperature control issue.
Initially, I experienced the problem with multiple W600 thermostats paired with FP300 sensors.
Before purchasing, Aqara Support had explicitly confirmed to me in writing that the FP300 was compatible with the W600 for native external temperature regulation. However, Aqara has since reversed that statement and informed me that the FP300 cannot be used as an external reference sensor for the W600.
I therefore purchased both a W100 and a Temperature and Humidity Sensor T1, which Aqara officially supports for native external temperature regulation.
Unfortunately, the exact same issue persists with both sensors.
The W600 correctly displays the external temperature in Aqara Home, but the radiator valve still appears to regulate according to the W600’s internal temperature.
I have tested multiple W600 devices with different external sensor combinations, with the same results.
My complete setup and firmware versions:
- W600: 0.0.0_2848
- W100: 0.0.0_1641
- T1: 0.0.0_0029
- FP300: 0.0.0_6542
- Hub M200: 4.5.80_0007
All devices are connected via Zigbee through Aqara Home.
My radiators are installed inside enclosures, so the temperature around the W600 can be significantly higher than the actual room temperature.
This is why I specifically chose a system advertised to support native external temperature regulation.
The external temperature is displayed correctly, but it does not appear to be used reliably for the actual valve regulation.
I have requested that Aqara escalate the problem to its firmware development team.
Has anyone using W600 firmware 0.0.0_2848 found a reliable workaround or received confirmation of a planned firmware fix?
I would particularly appreciate feedback from users who have tested the W600 with a W100 or T1 as the external temperature reference.