I am just starting this endeavor and trying to replace my existing proprietary control system without pulling wires…
I use a hydronic radiant based system for heating and cooling and each room has a thermostat and one or more valves on a manifold, depending on its size. There are 3 different pumps with mixing valves adjusting the temp of the liquid moving through each respective manifold. The pumps and mixing valves are colocated while the manifolds are spread out.
The ideal state is to open/close a given room’s valve actuator(2-wire 24VDC), start/stop the relevant pump(2 wire dry contact) and adjust the mixing valve setting(2-10vdc) so outgoing water is above dew point.
Starting basic, since humidity is not an issue yet. Just trying to configure a W100 and having the setpoints from that engage a T2 to energize the manfiold actuator.
I believe the diagram below is the correct one, for the dry contact of the T2, substituting line power for 24vdc. L1 and LOut are connectedto the 2 wire actuator. Do I have that correct? The actuator is polarity indifferent, probably not the right word choice. There is not a manual switch, although in the future I might add a toggle at the manifold simply to support maintenance.
If I get this working, the pump activation is a rinse and repeat as is the powering of a dehumidifer/humidifer as the project evolves.
The dewpoint mixing vavle control is going to be the beast of it all, but at least it is formulaic automation…
EDIT to add a question:
Forgot to add a question about leveraging a multi-zone valve controller, akin to a Taco ZVC40x-5 or Tekmar 30xV(x being the number of zones), as it will energize the pump for the manifold and also activate air-side things without having to add automation complexity to the system.
Since those will power a thermostat with 24VDC, is there a way to wire the T2 to power steal from the controller? Wiring L and L1 with jumper between N and L2 or something like that?
Thanks in advance for the help.