W600 (WT-A03E, Zigbee 0.0.0_2848) keeps the room 1 to 2 C above the setpoint

Hi,

I have two W600 valves (WT-A03E) on Zigbee firmware 0.0.0_2848, paired to Zigbee2MQTT 2.14.2. Internal sensor, no schedule, window detection off.

The valve does not regulate around the setpoint. It regulates in a band that sits 1 to 2 C above it.

With the setpoint at 23.0 C, over 24 hours:

  • the valve opens (to about 16 %) when its own displayed temperature falls to 24.0 C
  • it closes when the displayed temperature reaches 25.0 C
  • every cycle repeats this, for example opened 23:42 at 24.0 and closed 00:07 at 25.0, opened 01:34 at 24.0 and closed 01:56 at 25.0, opened 12:07 at 24.0 and closed 12:29 at 25.0
  • an independent room sensor read 24.1 to 24.9 C the whole day

So a setpoint of 23 gives a room of 24 to 25. I understand the hysteresis is fixed at 2 C, but the band should be centred on the setpoint, not start 1 C above it.

Two requests:

  1. Centre the band on the setpoint, or make the hysteresis configurable.
  2. External sensor mode - I see the same as in this thread, the valve keeps following its internal sensor on 2848:
    W600 external sensor does not control valve – firmware issue

I can share logs or test a beta firmware.

Thanks

Ugh welcome to the club. It seems it will take a long time until those are fixed for some reason